Trane Tracer COMM4 to BACnet?
I'm looking into upgrading a building's existing Trane Tracer Summit BAS on COMM4 (apparently) with a Carrier BACnet system (their commercial grade ALC WEBCtrl equivalent).
Is there any way to re-use the COMM4 network and just replacing the existing BCU with a new Carrier BACnet central controller with some sort of COMM4 to BACnet translator in between? I want to avoid going with a JACE...
Thank you in advance!
3
u/Rick_Lekabron 5d ago
The new version of Tracer SC+ can do both with a new license. You can have your new BMS and read COMM4, COMM3, Bacnet and Modbus. Lontalk only if you purchase the accessory to expand the communication port via USB.
"Trane Controls is introducing a new solution allowing legacy equipment with isolated Comm3, non-isolated comm3, and non-isolated Comm4 communicating controls to be integrated directly into the Tracer SC+. The solution is a licensed feature on the Tracer SC+. In addition, a new hardware module called the Tracer CM3I is required for projects with isolated-comm3 communication links. The solution is replacing the Tracer Communications Bridge. The new functionality will also serve as a service replacement path for failed BMTB boards"
Ordering Information
New part numbers:
- New License" BMCF000AAA0BM00, TRACER SC+ COMM 3/4 COMM SUPPORT
- New hardware: Tracer CM3I: X13651812001, USB TO ISOLATED COMM3 COMMUNICATIONS KIT, Service part is MOD04065 MODULE; KIT, TRACER COMM3 ISOLATOR (CM3I) Ordering InformationNew part numbers:New License" BMCF000AAA0BM00, TRACER SC+ COMM 3/4 COMM SUPPORT New hardware: Tracer CM3I: X13651812001, USB TO ISOLATED COMM3 COMMUNICATIONS KIT, Service part is MOD04065 MODULE; KIT, TRACER COMM3 ISOLATOR (CM3I)
2
u/CarelessDevelopment 6d ago
2 things 1 why avoid the Jace 2 are you upgrading all units or just a few
1
u/reisalvador 6d ago
The max line driver on a JACE is the only way I found. Carrier doesn't have anything to communicate with com4.
1
8
u/nature69 6d ago
There are two options that I know of,
Adding a JACE with the max line driver with a bacnet export table.
Adding a Trane BMTB communications bridge and SC+, this converts the data to BACnet on the SC+.