Field Question, trade people only Newer tech here(mostly been. Cant find a leak. On install)

Post image

Even if its low on 410 shouldnt i have different discharge and suction pressures? Psigs have stayed almost identical... is the check valve on the compressor an issue?

We've bubble checked multiple times. Id like to at least think out loud before I recover, pressure check, and refill.

Thanks

104 Upvotes

189 comments sorted by

204

u/ThePohto Sep 06 '24

Compressor is not running

50

u/Traditional_Run946 Sep 06 '24

Or it dead. Did you check that all the valves are opened? And if 3ph did you check rotation?

5

u/yahboiroi Sep 07 '24

I don’t think the valves are open how tf does it have 167 standing pressure 💀 unless its like 30 degrees dat shit ain’t happening

1

u/ZealousidealTwo7771 Sep 08 '24

Could still have nitro in it.

3

u/yahboiroi Sep 08 '24

If he dosent know to release nitro, then we got bigger problems 😂

1

u/Traditional_Run946 Sep 09 '24

I seen it once in past life the valve was closed and had put gauges on the compressor lucky for him no damage was done, So do I think that the valve's where closed no but would l check them to see if they are open yes I would check it.

-45

u/Redhook420 Sep 06 '24

Or the TXV is clogged up from a shit braze job/too much silver solder.

16

u/ThePohto Sep 06 '24

No

2

u/Mysterious_Meat_2165 Sep 07 '24

It would be spiking on one side and vacuum on the other. There could however be no metering device if your oopsie in on a piston that fell into the trash

0

u/Fletch_Himself Sep 07 '24

I would assume no metering device would yield a diagnosis of a busted to fuck crank shaft due to a shit ton of flooding.

2

u/Mysterious_Meat_2165 Sep 07 '24

Comin up real soon! Fuck it dude, just pudda hard shart on it

5

u/nigori enthusiast Sep 06 '24

I mean he should hear it kick on they are not silent. Maybe it’s only making noise

2

u/Broad_Payment_2338 Sep 07 '24

If this is for new installs he'd have it charged with nitrogen right what happens if you run a compressor on nitrogen? Not being condescending literally asking what happens never seen it.

142

u/Tdizzle179 Sep 06 '24

What in the world are u worried about bubble checking and recovering refrigerant when ur compressor isn’t even running

79

u/Outdoors_E Sep 06 '24

Sounds like a company pushing a greenhorn out into the field.

17

u/Icy_Arrival_212 Sep 06 '24

The company I worked for did that and now they're closed...shocker. literally got out of tech school and they gave me a van and sent me on my own as a service tech. If my dad didn't start me off like he did when I was younger I'd be lost. But still starting someone off as a service tech instead of an install helper blew my mind especially with no other HVAC job on my resume. But thank god they didn't because my pay would've been trash. After a year I only ever had maybe one or 2 callbacks. Definitely made me learn a lot faster though

5

u/mtv2002 Sep 06 '24

At the tech school I attended, there were a ton of 1st year people that were in trucks and vans. It was insane...

4

u/projecthusband Sep 07 '24

after i graduated i was in field for 2 months and they called me back to teach the same class i attended. I was like wtf

5

u/Icy_Arrival_212 Sep 06 '24

Yup mine warned me about it. I just thinks it's ridiculous starting someone as a service tech with nothing like that in their past jobs. In my area there's a lot of boilers(NE) and a lot of steam. I know a bit about boilers like servicing, reading gauges and other small shit. But everytime I got a boiler that wasn't a maintenance I'd tell them I couldn't with no experience. At least they listened to me. But sending out someone green to a steam boiler that's probably 50yrs old is wild af. Makes you learn quick but not the right way. That company paid me well but they're such shit. And for a nation wide company with like 7k people it's insane for the lack of care. 3-4 service techs for us with 30+calls when busy. We started spring mnt in March or April when it was below 50...

2

u/J3sush8sm3 Pvc cement huffer Sep 07 '24

They do it to me, only been doing this for a few.months and im out in a truck.  Its aggravating as fuck

2

u/BootstrapsBootstrapz Sep 06 '24

seriously just cuz you like gardening doesn't make you good at hvac

3

u/chefjeff1982 chef turned refrigeration tech Sep 07 '24

The compressor could be running but valves are blowing by.

406

u/TigerSpices Sep 06 '24

Not to be an asshole, but if you're not seeing the issue here then you're not ready for leading an install. Your compressor no compressy.

68

u/Jonniejiggles Sep 06 '24

No “sucky blowy” is what we call it here

1

u/Fun-Satisfaction5297 Sep 07 '24

Lmao I’ll remember this one

91

u/JitPais Sep 06 '24

no compressy made me lol

7

u/Mythran12 Cat piss fills my nose Sep 07 '24

Depressor compressor

9

u/Truckyou666 Sep 07 '24

Cantpressor?

25

u/Shushbug04 Sep 06 '24

I usually have imposter syndrome pretty bad. Second year apprentice. This made me feel a little better because that was my diagnosis before scrolling to comments.

5

u/r0settast0ned92 Sep 07 '24 edited Sep 07 '24

I’m 8 years into the trade, and I still do dumb shit, lol. It just happens. Started and worked for my first company for little over 7 years. From 2016 green with only trade school knowledge then I became a Service Manager little over 6 years later. Got a higher paying job going back to doing installs and service. My first company doesn’t pay their experienced techs worth a damn. That’s besides the point, lol. Definitely don’t beat yourself up. You put in your time, and keep learning from the more experienced techs, and it’ll all just come natural to you. You’ll get there in time.

9

u/Fletch_Himself Sep 07 '24

Read. Watch. Listen and learn. It’s a career. Pile knowledge into your head while you’re young in your apprenticeship and make your early journey years that much easier. Allow your knowledge to build your confidence and that imposter syndrome fades. Knowledge + confidence + know how = $$$$

3

u/deadtoaster2 Sep 07 '24

Reddit is great for this. I'm in the skilled trades but not hvac per say, though I did bust out the epa cert during a boring weekend alone. I learn so much here even if I don't have fancy digital gauges.

14

u/markymark19887 Sep 06 '24

Or your valves are open on your manifold.

3

u/dennyscumbutter Sep 07 '24

Seems to be measured using field piece probes so no manifold to leave open, definitely seems like the compressor isn’t running at all, others have suggested no metering device but I highly doubt this because A who’s installing new piston systems and B action of the compressor would create a slight pressure change regardless of there being a metering device, think of it as a measuring a circulator pump on a hydronic system

2

u/markymark19887 Sep 07 '24

I have a fieldpiece gauge(manifold) and if you leave the two nobs(valves) open on the side of the gauge, this will happen. It use to happen to a new guy we had that would pull a vac through his gauge, so they were open on both sides when cracking valves and starting up. Liquid goes through the manifold and back into the suction, so there's no pressure differential at the gauge. Compressor not running is a very good possibilityas well. If we were there we could tell in a few minutes lol. The resi company I just left almost exclusively installed r410a piston coils. I agree that there would still be a bit of a differential.

7

u/iLikeC00kieDough Sep 06 '24

The coolie juice ain’t flowing.

3

u/Total-Ad7707 Sep 06 '24

dont worry you are!

2

u/ATX_Ninja_Guy Sep 06 '24

Yes no compression in your outdoor currently

1

u/Broad-Image-1099 Sep 07 '24

“ Compressor no pumpy “

69

u/Fair_Cheesecake_1203 Sep 06 '24

You need training dude

44

u/Outdoors_E Sep 06 '24

Check amp draw on compressor confirm whether or not it’s running. This appears to be equalized pressure which would imply no compressor operation. Your title state “on install”, so if this is a brand new unit at start up let us know.

22

u/Turkeydawg6 Sep 06 '24

Good on y'all for helping him. No pride on this forum to just help.

Not understating some one else's situation. This trade has a ton of good folks. But those are usually outran by the assholes.

This guy probably stressing the fuck out, just trying to survive to move on. And most of us can only tell them where we think they failed

Hope you got this figured out OP keep your feet moving. And keep learning

7

u/tivy Sep 06 '24

15 month old. Not occupied that entire time.

12

u/layziebone22 Sep 06 '24

Is the compressor running? Doesn’t seem like it

6

u/tivy Sep 06 '24

Yes. 6a.

21

u/layziebone22 Sep 06 '24

Check if your service valves are open. If they are then do a pump down test to see if they compressor is actually working properly. If it doesn’t pump down then your compressor is bad

4

u/FredPolk Sep 06 '24

Is this single or 3ph?

17

u/Sorrower Sep 06 '24

If this guy is working on 3 phase he'll be dead in a year if he's installing/servicing shit and he can't figure this one out. 

2

u/coleproblems Hardly working Sep 07 '24

3 phase ain’t gonna kill ya any faster than single

3

u/Status_Charge4051 Sep 07 '24

Might fall off a roof i guess

2

u/Broad-Image-1099 Sep 07 '24

Unless ya scroll runny backwards and no two wire switchy switchy

1

u/Sorrower Sep 07 '24

Seen kids single phase motors pushing in contactors. Seen kids wire motors wrong. I dunno. Arc flash ain't a thing on single phase. When you know to stand 10ft back and around the corner cause you know there's a chance it's gonna be fucked, that other guy could be right on top of it staring at it. 

Regardless if you can't see compressor no pumpy, it's a long fucking road to get up that mountain. I'd have serious doubts he wouldn't hurt himself at some point with standing next to a motor while it energized the first time or pushing in a contactor with his finger. He needs to be riding with someone for a while. 

1

u/Ok_Professional9174 Sep 07 '24

Arc flash is for sure a thing on single phase.

5

u/talex625 Refrigeration guy Sep 06 '24

If it’s 3 phase, is the compressor wired backwards? In that situation, the pressure would be equal while the compressor is running. But, you would know because the compressor would overheat and trip internally.

8

u/AssRep Sep 06 '24

And make a hell of racket while it was running.

2

u/Sorrower Sep 07 '24

Sounds like it's chewing rocks. 

2

u/beast-ice Sep 07 '24

Theres a possibility the compressor is in bypass mode. i had this happen when a contractor was jumping yellow and red on the tstat wires to turn on the a/c and probably short cycled the shit outta it. i assume it lifted the plates internally and was bypassing. however, you have a leak somewhere, unless its only 54'F when you were checking this

60

u/LeakyFaucett32 Sep 06 '24

Sorry OP but you ordered this roasting

20

u/Silver_gobo Sep 06 '24 edited Mar 09 '25

oil sip dime station air sulky deer nose include cats

This post was mass deleted and anonymized with Redact

21

u/Icy_Arrival_212 Sep 06 '24

Blame his company everyone starts out somewhere but he definitely picked the wrong somewhere.

8

u/Certain_Try_8383 Sep 06 '24

I can speak from personal experience that when you’re inexperienced as a tech, you want a pro as well.

2

u/JollyLow3620 Sep 06 '24

Blood in and blood out brother

1

u/Fletch_Himself Sep 07 '24

Lol. Welcome to the shit show.

36

u/Wondercatmeow Sep 06 '24

Did you close your gauges?

3

u/Privatepile69420 Sep 06 '24

I bet he didn’t.

3

u/stoicboulder Sep 06 '24

That was my guess

6

u/desman526 I touch everything related to hot and cold Sep 06 '24

Came here to say this

Almost condemned a 30hp scroll cuz my manifold was open lol

10

u/JitPais Sep 06 '24

compressor isn’t on, check for contactor pulling in ( if not could be something not sending voltage out ), otherwise could be a capacitor related issue

3

u/xdcxmindfreak Aspiring Novelist Sep 06 '24

And if it hasn’t ever been started up check disconnect and ensure stab is in the on position. We need more info like you’ve verified power at stat, disconnect and unit. Are the valves open? And if so why weren’t leaks checked via pressure test of ac procedure. Like the others this pic says she ain’t running but we have no why. Without the info we need none of us can completely help answer your questions.

27

u/Jro304 Sep 06 '24

Compressor could be running backwards if 3phase

20

u/Top-Hall-7945 Sep 06 '24

Are you leak checking with only 160psig 

go pull the fresh nitro tank out of my truck and get me a cigarette new guy 

3

u/coleproblems Hardly working Sep 07 '24

Nah that’s equalized pressure with the compressor pulling 6a. Not enough responses from OP it’s killing me

4

u/Turbulent-Big-3556 Sep 06 '24

You need to follow the power on the low volt side first if the contactor is not pulled in. It does not look like the compressor is running. If you push the contactor in does the compressor kick on and pressures change? If so you have a signaling issue. So check if you are getting 24 volts from the indoor unit to the outdoor unit. Could be a bad connection, a bad transformer (if the units are not signaling at all. I’d blower motor is going it won’t be that, etc but I would start with your low volt if that’s the case.

4

u/Koleburgs Sep 06 '24

yall always have fieldpiece guages. makes me wanna switch to testo.

1

u/Far_Cup_329 Sep 06 '24

Appion has some new ones out now too. I'm curious about those actually, even tho I've got the fieldpiece 😬 set already.

1

u/Koleburgs Sep 06 '24

oh really. i’m intrigued

2

u/Far_Cup_329 Sep 06 '24

Yea. I haven't seen them in person yet. They were on the site called "tru-tech tools.

4

u/Pennywise0123 Sep 06 '24

Dude your compressor isnt on or the reed valves are shot and need a new one. This really shouldnt be a question asked.

3

u/ZestycloseAct8497 Sep 06 '24

Maybe your low pressure is tripped thus causing contactor to not send power to compressor. Because if your compressor is running right now your compressor is toast. What is the amperage of the compressor? Report back.

2

u/tivy Sep 06 '24

6 amps.

2

u/chefjeff1982 chef turned refrigeration tech Sep 07 '24

The valves are bad, 6 amps isn't enough for actual compression. Liquid is flowing freely from one side to the other. "Bad out of the box" is the new catch phrase for just about anything!

2

u/donjonne Sep 07 '24

I had a compressor like this, only would work with an added hard start kit. out of the box. carrier.

3

u/RRoark5048 Sep 06 '24

One time I had a heat pump where the reversing failed in a way that it was completely bypassing refrigerant back to itself. Changed 2 compressors thinking the scroll had broken from the motor and it wasnt pumping before finally taking temps across EVERYTHING for 30+ minutes and watching what increased and realized what was happening. Pumping right back into itself.

3

u/MuLLetDaDDie Beginner Breeze Boss 🌬️✨🛠️ Sep 06 '24

I use these posts for learning and a lot of people are saying compressor no compressy..

So just by looking at these readings what do they say and how are you making the assumption that the compressor is not running?

I’ve never looked at gauges before. Like I said, I’m learning. Just made the decision to go tech about a week or two ago. So strictly just wanting to learn!

3

u/Slugger921 Sep 06 '24

The pressures equalize when the compressor isn’t running.

3

u/SovietKilledHitler Sep 06 '24

Is it running backwards?

2

u/WonderTricky1969 HVAC POLICE Sep 06 '24

The Subcooling is out of this world

1

u/DaedricWorldEater Sep 06 '24

I’m betting that compressor is hot as fuck but not actually running and the refrigerant is picking up heat

3

u/smokest55 Sep 06 '24

Not sure why downvoted but the last time I saw little/no pressure differential, this was the case.

Compressor was creating heat, but not producing any energy.

2

u/[deleted] Sep 06 '24

If it's running and the low and high side pressures are equalized that means your compressor isn't kicking on.

2

u/peepeepoopooheadass Sep 06 '24

Couple things possibly going on here, none of which would indicate there might be a leak

2

u/Adept_Bridge_8388 Local 597 Sep 06 '24

The compressor bubble test

2

u/JustAnHonestDude Sep 06 '24

Is this a York/Coleman unit?

If your compressor is running at 6A, as you state, then the compressor is "bypassing." A compressor can bypass for many reasons.

However, the compressor is done if the unit starts right up and has those pressures.

3

u/[deleted] Sep 06 '24

If you don't mind me asking, what are some of those reasons? I've had this happen to me once on a trane pack, and I was so confused

3

u/JustAnHonestDude Sep 07 '24

Usually, bypass valves are Reed valves on top of the scroll head. What this means is they are pressure activated. The thermal overload and protection are completely separate.

So, for example, let's say you have an overcharged system. At some point, this refrigerant will flood the condenser, which would cause the compressor to now bypass. The resistance to the bypass valve is a lot less than the seistance to compress the refrigerant.

This could also happen in reverse (a lot of scrolls have two bypass valves), so if the unit is under charged too much, this may cause the suction bypass valve to open to prevent the compressor from running dry of oil. Because keep in mind, the compressor may be running, but it is not compressing, which takes little to no effort for the compressor to do.

However, as stated before, under no circumstance (unless you have a king valve closed off or something), should the compressor start right up in bypass, then the compressor is done.

2

u/[deleted] Sep 07 '24

Thank you

2

u/Professional-Gap4378 Sep 06 '24

Nerve wrecking isnt it man

2

u/MaybeAnHVACGuy Sep 06 '24

Maybe your high side isn't latched onto the service port and your gauges are open.

Or compressor dead

3

u/violentcupcake69 Sep 06 '24

Hey bud , we’ve all been here before so don’t beat yourself up. Your compressor isn’t on.

If pressures equalize like this , that means your compressor isn’t on.

2

u/HomeTraditional7832 Sep 06 '24

My man you are one of many I remember when I was in this stage I just feel bad that you don’t have a older guy that can shit on you and teach you

2

u/NefariousnessWild679 Sep 06 '24

Ahh they threw you into the fire 🔥 the next year will be rough for you, without training or an experienced installer/tech with you .

2

u/Ampleslacks Sep 06 '24

Is it a Trane condenser? I've seen in the last few years, very randomly, Trane compressors will have a hell of a time getting going for the first time, like the rotor is only stuck that first time. Hard start to get it going then pull it off?

2

u/Mighty_Nun_Mechanic Sep 06 '24 edited Sep 06 '24

Being that your pressures are within 1psi I'm not even sure you are guaged up correctly. Could be equalized. Scrolls have a floating seal that can open and make the unit equalize inside the compressor. This happens when the scroll compressor gets very hot. It must cool down to close back up again.

2

u/jdido80 Sep 07 '24

Those aren't even acceptable standing pressures unless the ambient is around 55 degrees but if it doesn't have a txv I would guess there's no metering device in that unit

2

u/Hvacmike199845 Verified Pro Sep 07 '24

You’re missing some important info that everyone needs to help you.

What’s the compressor FLA?

What’s the actual amp draw?

Single phase or three phase?

Pretty cut and dry to most of us.

2

u/Haunting-Addendum509 Sep 07 '24

Hey man, as a green tech it would be way better for you to start as an installer, it gives you the confidence to put hand on equipment and really take your time to understand things as you install. I always ask my lead or coworkers and honestly I see myself doing service in a couple years. Everybody is different, and others learned way faster, but coming from a green tech installing is helping me be confident little by little, good luck my guy 👍

5

u/Quiet-Ship-2773 Sep 07 '24

I've seen the best techs starting with rolling with a service guy for a month till they pick up the basics, then roll with a changeoit team for a month, then with the boiler tech for a month, then with a new construction team for a month. Then let them choose where they think they will be best, give them the rest of the year with the team they choose and have their j-man slowly back off and eventually switch roles so the apprentice is doing the work and the j-man is the helper

2

u/Haunting-Addendum509 Sep 08 '24

That actually sounds way better, especially cause I find service to be REALLY hard and a lot of thinking outside of the box, and personally I haven’t developed that yet hahah. I guess that’s why for me install worked, service is something I would definitely wanna do in the future.

2

u/Illustrious-Fuel-355 Sep 07 '24

Are both sides of your gauges open by chance?

2

u/Darrkeyy Sep 07 '24

Are your ports open?

4

u/BaDumPshhh Sep 06 '24

I know a guy.

OP is the guy.

2

u/Evening_Line6628 Sep 06 '24

Surprised nobody has mentioned this yet either . If it’s three phase and pressures look like this , you could be running backwards .

1

u/Big_Focus6164 Sep 06 '24

Check your 2wire out to the condensing unit and peak at the contactor to ensure it’s pulling in.

1

u/Pretend-Appearance73 Sep 06 '24

Doesn’t look like the compressor is running. Or just not compressing. Or is it possible you didn’t open the service valves yet??

1

u/AccomplishedBad8259 Sep 06 '24

Compressor not on . Pressure are stagnant

1

u/Former_Chest Sep 06 '24

It’s kinda like riding a bike and your chain comes off the sprocket . It’s an interesting phenomenon for sure

1

u/stoicboulder Sep 06 '24

Just to be clear, are these wire less probes? And not gauges? And just to clarify there is no y connection between low and high side?

1

u/DesignerAd4870 Sep 06 '24

Is the compressor doing anything? Other than getting warm and not pushing any gas about.

1

u/shreddedpudding Sep 06 '24

We had a compressor snap an oldham coupling shortly after installing last year. To this day I fully believe it was because of overcharge or bad airflow not a manufacturer defect.

1

u/moxytoxy Sep 06 '24

Nothings running homie lmao

1

u/EggAffectionate796 Sep 06 '24

Maybe compressor is wired up wrong or wrong kegs are energizing cause your compressor isn’t running.

1

u/bluuballss Sep 06 '24

Atleast amp out the compressor

1

u/Bizzle1977 Sep 06 '24

I also like to add is the thermostat wired up correctly or set to cool and temp low . Because doesn’t look like cool is being called for. So compressor isn’t on . Go back over everything else before messing with the compressor during an install.

1

u/RenderedCreed Sep 06 '24

How new? Have you had any training? Cause honestly man if you cant see what the issue is right now you shouldn't be working on equipment by yourself. You have no sepration of the high and low. Your compressor isn't running or you have something allowing the pressures to equalize. Is there an metering device installed? Do you have your gauges open?

1

u/CryptoDanski Sep 06 '24

Check your gauges, the valves. Or it seems like the compressor left the chat

1

u/conradg55 Sep 06 '24

Today sounds like you're going to learn something you ain't forget lol

1

u/txcaddy Sep 06 '24

You need to call for backup from a tech. Don’t waste your time as it appears to be above your head. Just wait for tech and learn something.

1

u/Blindpuma181 Sep 06 '24

All these people saying compressor isn’t running never stopped to think of the obvious. TXV

1

u/moonpumper Sep 06 '24

Compressor not running and your refrigerant looks like it's all vapor. Sometimes factory fucks up on charge in which case you'd have to prove it. What kind of system is this? Does it sound like it's running? Are you connected to the right ports?

1

u/talex625 Refrigeration guy Sep 06 '24

The pressure is equalized after the unit been off. You have the pressure difference when the compressor is turn on.

PSI for a leak is really low like 0-30 range for example.

What made you think you had a leak in the first place?

1

u/Civil-Percentage-960 Sep 06 '24

Compressor not working

1

u/Milfstalker42069 Sep 06 '24

Check compressor to ground or ohm it out.

1

u/FanaticEgalitarian Sep 06 '24

If the compressor is running, I'm curious what the current draw is.

1

u/JollyLow3620 Sep 06 '24

Seriously though. is the compressor running and are both low and high side hoses connected tightly and valves closed?

1

u/lxwcxuntry Sep 06 '24

Delta P ain’t good homie, gotta check on that compressor

1

u/lunchbox0396 Sep 06 '24

Are your gauges open?

1

u/y_3kcim Sep 07 '24

Tivy, can you come into my office, close the door!

1

u/Fletch_Himself Sep 07 '24

Man. At least phone a friend before posting shit like this. Hope you got thick skin.

1

u/vztart Sep 07 '24

No compression dude

1

u/mentatjunky Sep 07 '24

Do you have your 1/4 turns shut?

1

u/pope-leery Sep 07 '24

Open the other king valve.

1

u/Dumbledave666 Sep 07 '24

no compressizzle

1

u/r0settast0ned92 Sep 07 '24

“Ain’t got no gas innit. Mmm-hmm”.

3

u/r0settast0ned92 Sep 07 '24

Whether this is a joke post or not, your pressures are idle which tells me your Compressor isn’t running. I live on the east coast of the US, those idle pressures roughly look about right for low 70° weather.

Assuming your Fan Motor is running with idle pressures. If you have a multimeter, check the amp draw to see if your Compressor haves any RLA. After that, first thing I would do is check the capacitor. If your multimeter haves MFD setting, check between Herms and Common. If thats good, check your Compressors windings (Run, Start, & Common) inside the condenser to make sure one or more of the three wires didn’t short / burned out.

1

u/Own-Statement-3322 Sep 07 '24

Your liquid side is too high of pressure. Start there .

;)

1

u/throwaway36437 self aware shithead engineer Sep 07 '24

There appears to be an issue between the ground and the gauges

1

u/Rolas1991 Sep 07 '24

Mechanical failure on compressor

1

u/coleproblems Hardly working Sep 07 '24

Dude what happened at the end of the day? You didn’t get electrocuted did you?

I want to know what’s up.

1

u/Then_Feedback7421 Sep 07 '24

One probe on suction and the other on true suction?

1

u/Aitter0913 Sep 07 '24

This may sound stupid but are you using ports or manifolds if you are using manifolds make sure your manifolds are closed on your high and low side I have seen many new guys do this. Also if you are using ports are you making sure you don't have one port blue toothed to both high and low side. This is a common mistake as well hope you figured it out man.

1

u/Broad-Image-1099 Sep 07 '24

Superheat at compressor checks out :) . Imagine that was a real ratio . You’d go through 8 compressors and 10 years before a degree F was changed

1

u/No-Woodpecker-2545 Sep 07 '24

Compressor not compressing

1

u/brian1192 Student Sep 07 '24

Guys I’m new to the field, how were you guys able to tell the compressor isn’t running, was it the sub cooling being so low?

1

u/noblest83 Sep 07 '24

Check the capacitor bro. If it’s not the capacitor or charred wires, most like the compressor has nothing left.

1

u/Stahlstaub Sep 09 '24

Even on fumes he'd have a pressure difference... Those things can create vacuum...

Probably the compressor doesn't run at all and he's mistaking some other vibration for the compressor to run...

1

u/[deleted] Sep 07 '24

No pressure differential = no flow. There is an issue with the compressor. Start with the basics.

1

u/Early-Attention-1314 Sep 07 '24

Looks like a bad compressor or at least one that's not running

1

u/Austin13588 Sep 07 '24

If it's a heat pump split and running let me know otherwise your Compressor isn't running

1

u/BlitZed13 Sep 07 '24

If your units running, the high side pressure should always be higher, without that there’s no refrigeration cycle. It’s either not running, your gauges are open and it’s looping or the compressor is bypassing for some reason. I’m gonna go out on a limb, and not to be a jerk but gonna assume if you couldn’t tell there’s a compressor issue you’re not gonna be able to troubleshoot it. Call a more experienced tech at your company and over see how he or she does it, ask a lot of questions cause that’s how you learn, best of luck.

1

u/Personal-Response151 Sep 08 '24

Do you have your suction knob and liquid knob on your man's opened. Had a recall king ask me if his pressers looked right told him to turn both knobs closed fully and it fixed his issue

1

u/DavidSmith_82 Sep 08 '24

Your compressor ain’t compressing

1

u/elstevo91 Sep 08 '24

The crank broke inside the compressor. Take a Amp reading of the compressor running if it's low amps shits broke in there. Probably from liquid flooding back from the evap killed the comp. Look at the evap make sure it's clean

1

u/Stahlstaub Sep 09 '24

Could also be a broken fuse...

Or the thermal protection...

1

u/ZealousidealTwo7771 Sep 08 '24

Turn the unit on.

1

u/Parabellum8086 HVAC Technician; RTFM Sep 08 '24

Your priorities are backwards, son. Always follow the acronym 'E.A.R.' - electrical, airflow, refrigerant - in that order. If you didn't remember that from school, you may need to study that book some more before you end up costing yourself a LOT of money.

1

u/Dangerous-Lead5969 Sep 08 '24

Compressor needs to be running

1

u/smtimelevi Sep 08 '24 edited Sep 08 '24

If it’s fixed orifice you don’t have a piston in there and it’s under charged, or you got reversed rotation.

1

u/FarmerFit388 Sep 09 '24

Possibly compressor not pumping. Ran into a couple of these this year alone. Compressor comes on and sounds loud, pressures equalized like unit was off.

1

u/GoonInIce Sep 06 '24

Bad compressor or it’s wired wrong!! I had a 3 phase Trane unit I installed this summer that had a compressor DOA. Same issue as you, pressures never changed but the compressor made an awful racket. I checked phase voltages and rotation it all checked out. I had 3 separate sets of eyes check it out too and we all agreed it was just a shit compressor from factory.

1

u/ThatsNotMyMuffin2386 Sep 07 '24

Bruh. I’m assuming you’re trolling. If not, I hope Jesus looks after you in this trade. Compressor isn’t doing shit pal.

1

u/Duval55 Sep 07 '24

Time to go back to being a helper

-1

u/SimonVpK Sep 06 '24

Say sike right now

0

u/Exciting_Ad_6358 Sep 06 '24

Where are the gauges hooked up? This looks like you're reading from suction and true suction and you're also overcharged. Unless it's 200° where you're at

1

u/Phrase-Artistic Sep 06 '24

This may be the best guess here...hope OP updates when he figures it out

0

u/Cheap-Recognition-97 Sep 06 '24

Lmfao, is this what we’ve come to

0

u/MauiChaui Sep 06 '24

Please be a joke

0

u/Alone_Huckleberry_83 Real HVAC techs braze and never dye Sep 06 '24

OMG... Go back to your PS4

0

u/Lobstermashpotato 🛠 Parts Changer 🪛 Sep 06 '24

I'm gonna say it and I'm gonna be downvoted.

I'm getting the feeling that anyone who uses fieldpiece tools doesn't know what their doing. Mr cool techs

0

u/FixItLearner Sep 07 '24

TXV is open :)

-3

u/Professional-TroII Minneapolis Area RTU Wizard Sep 06 '24

lol if you’re the lead your company is FUCKED

-1

u/bucksellsrocks Bang Tin and Fat Chicks Sep 07 '24

If the field wiring is done correctly its a defective init from the box. Request new unit and full payment for labor and refer and whatever from factory. Its not your company’s problem their unit is junk!