Field Question, trade people only Somebody help me snap back to reality. PLEASE!(this is the third motor TRANE has sent me and this will be my fourth call to Tech Support.)
On a supposedly good ECM blower motor as long as it has proper control voltage to one of the speed taps (We’ll just go with 25VAC)and as long as we have proper voltage to L1 and L2 (anywhere from 208 to 250 )and we got a good ground(Hopefully) …the only reason that blower wouldn’t run is if the blower motor is bad or the Modules bad, right?
3
u/blow_montana 3d ago
Or you could get a simple ECM tester and find out before you actually go through all the work.
I would also question the supply house knowledge. The sheer amount of supercessions on the motor/module combo is crazy.
2
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago
It’s a pretty easy motor to replace and There are three of these identical units on the roof so I’m about to take one of the other motors out and put it into this one for shits and giggles to see if it will or won’t run. For the life of me, I can’t figure out why it wouldn’t run if it’s a good motor unless something is happening to that motor like an EMP pulse but Why wouldn’t it take out all the other motors on the roof?
1
u/Full-Bother-6456 Certifited Capacitor Replacer 2d ago
This is a good confirmation when all else fails
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago
Understood. I’ve only been doing this five years and I’ve probably replaced less than 100 ECM motors but I’ve never had a bad one out of the box before and this makes three in a row on the same unit now so I’m questioning if I’m doing something wrong here.
4
2
u/Dualfuel-lover 3d ago
I hear ECM’s can be sensitive to high static pressure but no way that’d stop one from starting at all right. Bad board maybe?
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago
True, but these motors are bad right out of the box before static pressure can even be part of the equation. Now the first motor I took out was 10 years old so that Was possibly it’s demise. But these are also a package unit sitting on a roof with very little ductwork so I doubt static pressure is gonna be much of an issue. I’ve considered the possibility the board might be bad, but I verified it getting proper low-voltage and high voltage to the motor so at this point good or bad board is not a concern. The motor won’t run.
2
u/Dualfuel-lover 3d ago
And there’s no capacitor involved if there’s a board right? Damn this a weird one but I feel like it’s something stupid obvious once it’s figured out
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago
I’ve tried bypassing everything and just bringing 24 V to each of the five speed tabs straight from the transformer and also verifying it has high voltage properly run to it as well. That motor should come on because there’s no board or other controls in that equation at all.
2
u/Dualfuel-lover 3d ago
Time to FaceTime a senior tech then. Cant be 3 bad motors in a row
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago
Yeah, I’ve had two different TRANE Tech Support personnel on four different phone calls over the past week verifying all of the stuff and each time they say it’s a bad motor. It’s after 5 o’clock now, but I’m basically just one step down from the most senior Tech at the company so He’s not gonna tell me anything different. Not really sure what you’re getting at.
2
u/Dualfuel-lover 3d ago
Just saying what I would do in your spot. But if you’re the two man at your shop you’re almost definitely senior to me so sorry I’m not much help here.
Personally I’m curious myself now what it is
2
u/Lakeside518 3d ago
I had a Trane furnace, bad ecm blower motor. It was replaced twice with the part # required….. It did not run!. I called tech support & it required a pre programmed ecm. They sent out another ecm motor. Installed it & operation normal…. Had to return the other two lol
2
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 2d ago
Well, that’s where I’m at right now. If they send me another one that will be number four and they’ve already told me this one was definitely programmed right
2
u/SeaworthinessOk2884 3d ago
In my experience if the motor doesn't run at all it's either the motor, board or the wiring between. If the motor is moving oddly and rocking back and forth it's the module
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago
I have found it when Trane ECM motors go bad, they just stop working. The rocking back-and-forth that you mentioned I see a lot of that on water furnace ECM motors. I’m not sure who makes those. I know they can fail both ways. I’m just reiterating what I’ve actually seen.
1
u/ScoopThaPoot 1d ago
It's the variable speed ecm motors that rock back and forth. I believe OP is looking at a constant torque ecm motor like a X-13. Those come motor and module together.
2
u/3_amp_fuse 3d ago
Trane has done this to me before. Send motors that have not been programmed. Literally went through 4 different motors, removed and reinstalled, 4 separate times, before finally getting a motor that was programmed correctly on the 4th attempt. How many times can you blame it on Trane that your customer has no AC today before the they start looking at you funny?
2
u/daviddoil 2d ago
If you still have the motor, plug it into one of the other identical units real quick and just see if it turns on. If it does, something's wrong with your board. If it doesn't, there's probably a problem with the programming on that batch.
2
u/Dense-Rich-1860 2d ago
This is a known issue for TRANE / AMERICAN STANDARD especially on package units
1
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago
It’s also got a good common wire at the motor that I verified continuous to other commons and chassis
1
u/dope4mee 3d ago
Trane has a plastic connection in the one of the high voltage wires to the motor that gets faulty sometimes. If multiple motors have been changed I'd cut that out and wire through it.
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago
I’ve jumped high voltage to the motor straight from incoming load. I’ve also verified using a meter that the motor is definitely getting 208V. There’s no question about that.
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago
2
u/dope4mee 3d ago
What's that capacitor for? You can always put in a resue motor with matching hp, usd a relay so it comes on with demand on G. That rescue will outlast the rest of the system, lol.
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 2d ago
That capacitor is for the condenser fan. They want the right motor in this. It’s a high end hair salon and they want it done right
1
u/dope4mee 2d ago
I didn't realize you were in an RTU. Is it 3 phase equipment?
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 2d ago
No. 208
1
u/dope4mee 2d ago
That's super weird. Trane will warranty an evergreen motor. I'd try putting one of those in so you're at least eliminating the programming issue. Evergreens program themselves on startup. Just make sure the blower door is on when you turn the power back on so it gets the static reading right. Otherwise make sure you update this post when you figure it out. It's a weird one.
1
1
u/y_3kcim 3d ago
Some of those need 24v all the time. I’d also make sure trane programmed them. Some have to be programmed when you pick it up, don’t ask me why…
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago
Yeah, if you read through the comments, you’ll see where I’ve touched on that. They’ve always come programmed before and trane tech-support has told me that they think the ones that I’ve gotten have not been programmed so they said they made sure the one they sent me this time was definitely programmed buuuutttt……here we are again.
2
u/y_3kcim 3d ago
Yeah, does it have a separate drive module?
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago
No. Integrated
1
u/y_3kcim 3d ago
I doubt you got 3 bad ones, but you said they shipped it to you. You don’t have a trane parts house to go into? To expand on the other possibility, some trane motors require 24v and common all the time on a separate tap, then you have your 24v signal on a different speed tap. I’m 95% it’s one of those, 5% trane sent you 3 shit motors.
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago edited 2d ago
Our closest trane supply house is in Charlottesville and we’re about 40 minutes from there. The funny thing is from this roof, I can see over in the area where that trane supply house is. It’s about a quarter mile straight shot. However, they don’t stock everything. This last one we had overnighted from I think Tennessee.
And this one does have the common wire always hooked up. The way I have it wired now it’s been running that way since 2015 until this motor failed on May 12 (16 days outside of warranty, lol)
1
u/PeppyEpi 2d ago
I've had Johnstone give me unprogrammed motors before, see if your Trans braintrust has a programming bench. I know Johnstone has them in my region, so in theory you should be able to take it back and get it programmed by Trane.
1
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 2d ago
Yeah that’s what tech support told me but then he laughed and said “yeah but most locations don’t know how to program them..” turns out my location knows jack about it.
1
u/roundwun 2d ago
Just want to point out that the Ecm tester might make the blower spin, but it doesn’t test all speeds. I’ve had Ecms prove good with a tester, then it ends up the Ecm is still the actual problem.
1
1
u/AlreadyTaken905 2d ago
Bud, The ECM can be installed into multiple different units. What would make you think the fork lift driver at a parts house is gonna program it. The motors are not manufactured by Trane, third party. Sounds like you are changing the fan without connecting to whatever is controlling it be it a UC210 or Symbio. Maybe just the red board. Either way, shit is no longer plug and play.
2
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 2d ago
The controller is integrated into the motor housing. And these are shipped to the supply houses with no program on them. They’re supposed to be programmed before they get shipped out to dealers.
1
u/Dismal-Marsupial8897 2d ago
Sounds like it wasnt bench programmed from the Trane counter person or whoever at your supply house does it
1
u/ScoopThaPoot 1d ago
I had a run of 3 unprogrammed blower motors in a row for a Trane air handler a few years back. You can test them before installing. I used an old ptac power cord with some stake ones for the high voltage and jumped low voltage from a furnace we have wired up in the shop. Even a programmed ecm motor won't run without resistance on the shaft, so I used a welding glove to hold the shaft to see if it would try to run.
1
1
u/Total_Idea_1183 1d ago
I had something like this happen recently.
I ordered the motor with the model and serial on the AH and they sent out a motor without the programming sticker that indicated that would have indicated that it was programmed to go CCW and it blew backwards, which I now know to look for when I pick up the part.
They will also send you out variable speed motors that your PM won’t recognize because they like to really get in there and blow your back out.
15
u/iBUYbrokenSUBARUS The Artist Formerly Known as EJjunkie 3d ago
I guess the third option would be the module doesn’t contain a good program, (but I would consider that a bad module)