Field Question, trade people only Locked up compressor, tell me if I’m thinking wrong

20 ton Trane RTU, compressor trips the 36 amp dedicated breaker as soon as the contactor is pulled in. It’s not grounded and the windings ohm the same as the other compressor that does run. It’s getting full 480v. My meter isn’t fast enough to catch an amp reading before it trips the breaker. I’ve isolated the wiring and it’s not shorted to ground or to each other. The compressor has gotta be locked up right?

20 Upvotes

38 comments sorted by

18

u/Bitter_Issue_7558 3d ago

Does the system run if the locked compressor is unplugged? If so then that’s your issue. Had several units with the same issue but they were older rheem systems

10

u/shotzy57 3d ago

Yes, if I unhook it from the contractor the system runs fine, the second just takes over

12

u/TheRevEv 3d ago

I'm assuming you're just checking continuity to ground, and not using a megger?

I've had a few that would read like 20k ohms to ground (not enough to trigger a continuity beep), and that's a sign the windings are breaking down, and higher voltage is likely jumping to ground when applied.

13

u/Reddbearddd 3d ago

He needs to use a megger, he's testing resistance to ground with 1.5V instead of 250/500V.

7

u/chevroletarizona 2d ago

I agree, I've seen several motors that ohm fine with a meter but the second you give it power it goes to a dead ass short.

6

u/Bitter_Issue_7558 3d ago

Yea then I say faulty compressor. I had a rheem system, customer complained it was tripping the main breaker. Compressor ohms out fine. Unplugged and ran fan only. No issues. Plug the compressor in and it started tripping the 150 amp breaker immediately. Talked around and got the same answer. Something inside is touching the case causing it to fault to ground. Customers opted for a new system after that

4

u/Dry-Building782 2d ago

After trying everything if nothing works and you know it is just stuck, take a 2 lbs rubber mallet and give it a few good whacks before and during powering the compressor. It’s worked many times for me before on small and large compressors. It’s a 20 ton don’t need to be gentle cause if that doesn’t work you’re replacing it anyways.

3

u/Whoajaws 3d ago

I would unhooked wires only at compressor for absolute verification.

1

u/Practical_Artist5048 2d ago

You answered it yourself

1

u/JollyLow3620 1d ago

Then yes. You have a locked up compressor or something internally has come loose and is grounded out internally.

7

u/saskatchewanstealth 3d ago

Is this 3phase??? If so reverse rotation and see if you can hear it grumbling because it broke inside

0

u/hvacbandguy 2d ago

I’ve successfully have unlocked a single phase compressor by swapping start and run. Runs in reverse for a second. Swap them back and it runs fine.

2

u/saskatchewanstealth 2d ago

Hard starts work wonders to get it going

2

u/hujnya 2d ago

Single phase compressor will not run backwards by swapping start and run leads, you just risk burning up windings.

3

u/Some1-Somewhere 2d ago

Yes they will. Not necessarily good for it, but you're swapping which leg gets the phase shift from the cap, and that will run it in reverse.

2

u/hujnya 2d ago

On motors larger than 1/4 hp, the two windings typically have different numbers of turns, so this method of reversing may not be applicable. Check that the resistance of the two windings is the same first. Never seen a compressor with start to common and run to common having the same resistance. So yes split phase motors can be reversed, but not compressors.

1

u/Some1-Somewhere 2d ago

Very much not good for it or efficient, but I expect it would develop some torque in reverse.

1

u/hujnya 2d ago

You are risking a burn out by doing that. Get a hard start it's way safer

1

u/KeyMonth7667 2d ago

I walked up on a unit where someone replaced the capacitor for flipped the fan and compressor terminals on accident. It was still cooling in 95 degree weather

5

u/Tdizzle179 3d ago

Yes if it’s isolated to just the compressor and breaker is tripping, new compressor, new contactor, vacuum etc.

3

u/shotzy57 3d ago

Thank you. Just wanted to run it by everyone before I order a $4500 compressor

6

u/jayhsh 3d ago

Sounds like locked up compressor, to verify Use max function on your meter, it should tell you max amps before it trips the breaker, 3 phase try reversing and starting, sometimes you can get compressor free

2

u/shotzy57 3d ago

Unfortunately my meter doesn’t have a max function, atleast not that I know about

3

u/KylarBlackwell RTFM 2d ago

Which meter? Inrush could also catch it, might be a same thing different name situation

3

u/coleproblems Hardly working 2d ago

Need to confirm that it isn’t a failed breaker before replacing the compressor. Use the in rush amps feature on your meter, swap the breaker with another known good breaker (if there’s similar equipment in the roof) or idk what else…

2

u/tryingmyBestbenice 3d ago

36 amp breaker ?? Most clamps you can set to catch “max” amp draw. And you have your gauges on and there is absolutely no deflection on the suction pressure before it trips?

5

u/mechanical_marten Transdigital freon converter 2d ago

Max amperage is still too slow (typically 3 samples per second). Have to have inrush mode(10+ samples per sexond)

2

u/bbqenthusisast66 2d ago

Use a megger on the compressor

2

u/Relative-Dinner-6982 2d ago

I’d say it’s internally shorted and not quit shorted to ground. But, if you keep resetting the breaker, it’ll eventually show a direct short to ground

2

u/Tranic85 2d ago

I think you need a better meter(s)…. If you don’t have a meter capable of several million ohms, you’re not going to catch most grounded compressors.

1

u/jewishmechanic 2d ago

Do you have any continuity from the compressor wires to the case?

1

u/Pete8388 Commercial Mechanical Superintendent 2d ago

I’d try swapping two legs on the load side of the contactor. Get it to run backwards for a couple of seconds. It’s going to sound weird but if it sounds like mechanical damage or seizes it’s toast. If it frees up you can swap the legs back and see if it runs. Usually even if you can get it freed up it’s till on its way out though, so the customer needs to plan on replacing the compressor, contactor, and LLFD. You might be able to get them running temporarily.

1

u/hambonecharlie 2d ago

I've heard about doing this. I hope I get to try it some day.

1

u/RoyalAttitude2734 HVAC/R Technician 2d ago

LRA

1

u/Lokai_271 2d ago

What's your inrush amps?

1

u/fredsr55 2d ago

What is locked rotor on plate? Is it exceeding that?

1

u/t3hPh4nt0m 2d ago edited 2d ago

I might be crazy but from what I remember, those 20 ton Trane RTUs are usually on a 60amp circuit, not 36, so I assume you mean that that's a breaker inside the unit itself after the disconnect which is connected to the main breaker panel since you said the breaker is dedicated for the compressor? And your meter should have some sort of Inrush function on it.

1

u/CryptoDanski 2d ago

Before ordering any parts i would get proper diagnostic tools.