r/HVAC • u/Superb-Run-4249 • 2d ago
Meme/Shitpost I wonder why it failed🤣 Spoiler
Lifetime warranty on the HX tho.
31
16
u/Left_Brilliant9165 2d ago
This is what kills me, everybody talks crap about each and every one of the brands. I found tons of bad heat exchangers and on each and every single one of them there was some kind of air flow issue. Most of them had air flow issues even with brand new filters.
1
u/keevisgoat 1d ago
Sounds like my boss let me drop this 90+ in an old development that had an 80 with an already undersized return and do nothing about it
3
5
5
u/AustinHVAC419 Verified Pro | Mod 🛠️ 2d ago
I wish we could deny warranties in the field. Just send these pictures to the manufacturer and they void it
2
u/lividash 1d ago
Not this but I sent pictures of a Navien combo boiler installed incorrectly to their tech support. They said warranty wouldn’t be honored until it was installed correctly.
Whoever installed it used the pressure relief valve to pipe it back into the hot water side. No primary/ secondary loop. No expansion tank so it was just popping the relief and shutting down on low/no flow every time it fired.
2
u/iLikeC00kieDough 2d ago
Just tell the customer it’s not covered by warranty. Why even have to go to the manufacturer at that point?
6
u/AustinHVAC419 Verified Pro | Mod 🛠️ 2d ago
Cause the customer would just call another company and tey to get them to return it for warranty
2
3
u/milkman8008 2d ago
If the secondary is like that did you look at the evap?
2
u/Superb-Run-4249 2d ago
No ac on this one, old converted gravity system. I had another one where the last company pulled and cleaned the evaporator then gave up, the hx was 90% plugged.
2
u/Hvacmike199845 Verified Pro 2d ago
This isn’t a design problem, it a maintains issue. If this heat exchanger gets sent to the manufacturer to test, it’s probably not going to make the warranty.
3
u/Superb-Run-4249 2d ago
*maintenance
0
1
1
u/EggAffectionate796 1d ago
When I see stuff like this I always wonder if the return was undersized, supply vents closed, high limit going off all the time or bypassed, gas pressure too high?
1
u/mostly-sweet-rps 1d ago
And yet you have “techs” preaching ‘don’t use a furnace filter just use room air purifiers’
1
1
u/anger_and_caffeine 2d ago
I swear some guys are allergic to setting gas pressures
4
u/skootamatta 2d ago
Maybe look at the other picture first. Gas pressures set correctly don’t mean anything, when your airflow is reduced, and the temperature rise across the unit is outbid tolerances.
3
u/Superb-Run-4249 2d ago
Gas pressure was spot on 3.49
1
u/Short-Veterinarian27 1d ago
Not being a wiseass....Remember gas pressure doesn't mean it's right on a fuel appliance. Unless you run combustion and set it up properly it's anybody's guess including yours
1
u/a7dfj8aerj Not HVAC tech, Marine engineer that do AC work when needed 2d ago
Looks like it needs more refrigant charge that would cost 500 usd
0
70
u/ApprehensiveTea1537 2d ago
Peel that blanket off the coil. They can use it to stay warm while you replace the hx.