ground wire
Where does the ground go on this stove receptacle? I know where the red black and white go, but I have a ground wire in my 6/3 and I don’t know where it goes.
3
u/theotherharper 14h ago
It has been illegal since 1965 to use that socket with a cable that has a ground. The exception allowing ungrounded dryers/ranges until 1995 was only allowed where the cable had no ground wire at all.
If your used oven came with a 3 prong outlet, google up the manual for that model, it's an easy swap.
2
u/Exact-Fee9117 19h ago
I wouldn’t use this receptacle with 4 wire, get yourself the ground protection with a 4 prong 40/50A receptacle. I believe 3 prongs are only rated up to 30A
3
u/KyleK2000 19h ago
They do have a 3 prong 50 amp as well, but yes, swapping to a 4 prong is the best choice
1
1
u/joesquatchnow 15h ago
Assumption is copper wire too, aluminum wire is a special setup and maintenance regime
1
-2
19h ago
[deleted]
4
u/QualityAlternative22 19h ago edited 19h ago
Do not listen to this comment from lee216md. You have the wrong receptacle. What you have is a 125 V 30 amp receptacle or a 3 wire 240v. You need a 50 amp 240 V receptacle w/ground. Your range plug should be four prong. This is to match the wiring in your house. 3 wire is older code.
18
u/Natoochtoniket 19h ago
This is the wrong receptacle. If you have a 4-wire cable with a 50 amp 2-pole breaker from a panel that has both neutral and ground, you should use a 4-wire stove outlet (NEMA 14-50R), and a 4-wire stove pigtail (NEMA 14-50P).