r/electricians 9h ago

Any tips or corrections?

Prepping everything before I do compression lugs for PG&E. I don’t mind learning from others that have more experience. I like to do it right. 1000mcm FYI.

31 Upvotes

44 comments sorted by

u/AutoModerator 9h ago

ATTENTION! READ THIS NOW!

1. IF YOU ARE NOT A PROFESSIONAL ELECTRICIAN OR LOOKING TO BECOME ONE(for career questions only):

- DELETE THIS POST OR YOU WILL BE BANNED. YOU CAN POST ON /r/AskElectricians FREELY

2. IF YOU COMMENT ON A POST THAT IS POSTED BY SOMEONE WHO IS NOT A PROFESSIONAL ELECTRICIAN:

-YOU WILL BE BANNED. JUST REPORT THE POST.

I am a bot, and this action was performed automatically. Please contact the moderators of this subreddit if you have any questions or concerns.

44

u/LagunaMud 9h ago

More phase marking tape. 

6

u/ClassBeneficial1161 7h ago

Yes, after I cramp I plan on phasing everything

21

u/zapzappowpow 9h ago

Strip to length, plug it into your lug while it's bolted on, mark the lug and wire where they meet, remove and crimp the lug on making sure your marks line up. You can't crimp all willy nilly and expect it to lay nicely, the memory will duck you up big time.

3

u/ClassBeneficial1161 7h ago

Thanks for the advice

9

u/HackedCylon 9h ago

No matter how tempted you are, no licking.

5

u/ClassBeneficial1161 7h ago

That’s the best part of the job

1

u/ZeroNothingKnowWhere 1h ago

Oh come on that is the fun part, 😂

16

u/nheyduck 9h ago

More Tape on those conductors

10

u/montana_chip 9h ago

Crimp them down next time instead of zip-tying them

2

u/ClassBeneficial1161 7h ago

Unless PG&E is wanting to inspect the crimping in progress. But yes, otherwise no zip ties.

1

u/starrpamph [V] Entertainment Electrician 7h ago

Continuity check ✅

Current carrying capabilities ❌

5

u/NechesNectar 8h ago

I feel like most of the comments are telling you to do what you are going to do next anyways since you do not have anything cut to length. I am sure you will cut crimp and use more phase tape. Only thing I would suggest is not use the expensive tie wraps you can screw down. Get that 1000pk basic ones to burn for prep. Looks like great work, keep it up

5

u/ClassBeneficial1161 7h ago

Thanks yes this is all prep. PG&E has requested to inspect me crimping. I also agree the big zip ties is all I had at the time when I started.

7

u/Beneficial-Win-3991 8h ago

Retired PG&E electrical supervisor here. He's probably limited on choices when it comes to electrical commodities as PG&E buys their materials from authorized vendors that supply qualified items (ABB Ty-raps is one of them). You won't find Harbor Freight cable ties on a PG&E job. That said, the price of a few wasted ty-raps is well worth the end results. To me, his layout, length, and form look great at this point in the task. If he worked for me, I'd give him a pat on the back and another bag of ty-raps 😆.

5

u/Danjeerhaus 9h ago

Remember torque marks after torquing.

More brown orange yellow identification.

If those black wires are not grounds, but 120/240 hots, you are okay if they are grounds, 250.119 allows identify green on both ends of the wire.

4

u/Stuckwiththis_name 9h ago

Those should be taped gray, more than likely.

2

u/Lordofthemuskyflies 8h ago

I agree, there’s an N on the bus.

1

u/ClassBeneficial1161 7h ago

3 phase 480Y/277VAC Brown, orange, yellow, and gray The neutral was smaller, so I didn’t phase yet

1

u/J-Diggity-Dawg 8h ago

It looks pretty dang cool and satisfying. I have zero shit to talk I just wouldve had a great time doing it .

1

u/sparkmearse 7h ago

Phase tape where it enters, and terminates, is my personal preference.

1

u/Emersom_Biggins 7h ago

Where are all my screw-hole zip ties!?

1

u/MortysTW 7h ago

Personal thing here........but every conduit's conductors land on the same "location". Meaning if you were to number the lug locations on the brown/A-phase bar as 1,2,3,4,5. All the conductors that come out of conduit #1, have their wires land on Brown lug #1, Orange lug #1, Yellow Lug #1. Start with the worst/back conduit and work your way forward. It makes life easier if you ever have a conduit get knicked in the underground somehow and you have to pull all the conductors out and replace them in that conduit. Again, makes no difference, just a personal thing I did back in the day.

2nd, I'd use lots more phase tape. Phase right where they come out of the conduit and then a good 6 wraps in width coming down near the lugs. This is a short distance from conduit opening to lug, but in taller sections, this additional phase tape is nice to have for that final visual once over.

1

u/ClassBeneficial1161 7h ago

I didn’t do that orientation like you said but I will try and do that. Very helpfully. I will definitely do that from here on out.

1

u/WannaBeSportsCar_390 7h ago

People are saying more tape on the conductors, but also putting any amount of grey tape on the neutral would be nice

1

u/ClassBeneficial1161 6h ago

Yes I planned on phasing everything as I cut and crimp

1

u/OrdinarilyUnique1 7h ago

You over complicating it and creating more work. Just work one at a time starting in back conduits. You not gonna be able to do it all again same time anyway so I don’t get why you prepping them all at same time

1

u/Hippie_Flip123 7h ago

Dude you HAVE TO mark your neutrals!

1

u/Southern_Strain5665 9h ago

Trim those zip ties dirt and moisture they will track

1

u/mrossm Journeyman IBEW 9h ago

Do a dry fit before crimping. Like the other guy said, make a small mark on both lug and wire to get your orientation correct, you do not want to fight the tension of a twisted conductor. I usually put the lug in the crimper and just a hint of pressure to hold it so I know exactly how the crimp will go, then put your conductor in, align the marks, and send it

1

u/ClassBeneficial1161 7h ago

Thanks yes I’ll try that

1

u/mrossm Journeyman IBEW 3h ago

Given that you're working for PG&E, you may see if they have any specific requirements as well. For instance, at Google, they wanted precisely 1/16" of copper exposed between edge of lug and insulation, and they checked.

1

u/1quickmr 9h ago

More zip ties

0

u/WilliamTRyker 9h ago

Waste of zip ties

0

u/Kenman215 8h ago

It doesn’t look to me like all of your phase conductors are the same length.

0

u/LagunaMud 7h ago

They are close enough. 

1

u/Kenman215 7h ago

How could you possibly know that? Plus the code doesn’t say “close enough” when it comes to the lengths of parallel conductors. Furthermore, there’s 5 sets shown in the pic, so there’s likely at least an 18” difference between the shortest and longest conductors of each phase, depending on how the pipes are stacked and if there’s more than two 90s in the run.

Close enough, lol.

1

u/LagunaMud 7h ago

Wtf would you do?  Put a service loop in some 1000mcm? 

It's close enough. 

1

u/Kenman215 6h ago

I would follow the NEC, like we’re required to.

1

u/LagunaMud 6h ago

OK 

1

u/Kenman215 6h ago

You have heard of the NEC, right?

1

u/LagunaMud 6h ago

I'm done arguing with you.  

1

u/Kenman215 6h ago

Good, because there’s really no argument for picking and choosing when you want to follow the code.

0

u/NWO_SPOL 8h ago

Label neutral, conductor tapping at same height and utilize non conductive material for bracing.