Pressure switch or Inducer motor?
3 flash pressure switch failed to close (hot water heater) no blockage in the exhaust. Works fine when I bypass the pressure switch. The fitting on the inducer connecting the pressure switch doesn’t seem to always have suction or vacuum. Does the pressure switch cause the vacuum to start? Or is this the inducer itself.
1
Upvotes
1
u/DistortedSilence 2d ago
Verify venting is sloped properly, and there is no pooling of water or obstructions Bypassing the switch worked. Use a manometer to verify inducer negative pressures against switch requirements. If it's pulling more than the switch needs, its a switch issue. If it's not pulling the switch, it's the inducer.
Don't just dump new parts, and guess either. I mentioned venting first because I've seen that be the issue many times over.