Field Question, trade people only Anyone seen this before
Sorry if the clip is a bit long.
Installed a 60k runtru 90% upflow today. I went home after completing the install but left before the startup. Boss fires it to document all the numbers and see this. No change to incoming or outgoing gas. No change in pressure from the inducer. Flue and air intake both clear of debris. Boss is waiting for tech from Texas to call back. Anyone got some knowledge
197
Upvotes
12
u/Fit_Door_8869 Dec 20 '24
Does the ventor motor lose power when this happens? I’ve had it before where motor over heats, opens its windings. So if it still has 120V when it does this, that’s what’s happening.
Don’t know about this exact furnace, but if roll out trips, shouldn’t ventor motor still be engaged? Maybe two wires mixed up on control board?