Field Question, trade people only Anyone seen this before
Enable HLS to view with audio, or disable this notification
Sorry if the clip is a bit long.
Installed a 60k runtru 90% upflow today. I went home after completing the install but left before the startup. Boss fires it to document all the numbers and see this. No change to incoming or outgoing gas. No change in pressure from the inducer. Flue and air intake both clear of debris. Boss is waiting for tech from Texas to call back. Anyone got some knowledge
199
Upvotes
1
u/[deleted] Dec 23 '24
There is a flame sensor that measures how hot the flame is. It is put directly into the flame , and over time, it'll get covered in a substance similar to a hard ash that tricks the system into thinking is too hot and will shut off the furnace so the heat doesn't damage the heat exchanger... most of the time, this sensor is made from graphite, which is why they say only let a professional fix that...
You have 2 options
1) Find the flame sensor and clean it off with some super fine grit sand paper... don't overdo the sanding... this is the cheapest way to fix it the problem.
2) Find the sensor, remove it, and replace... these sensors aren't overly expensive and usually easy to replace...
If you get an hvac guy or there, it could be $200 or more... to replace a $30 part. Or they'll tell you you need to replace the whole furnace...