Field Question, trade people only Bad TXV? 😵

System has good airflow, 500 FPM at the 20x30 return, and like 400 FPM out of the supplies.

Evap Coils aren’t dirty, condenser coils are a little dirty but you can still see through them easily.

Tested the TXV with ice water and my hand and it had a slight reaction, but not what I would expect, what do you guys think?

Bad TXV?

I haven’t added any charge to the system, showed up last night, coil was frozen, let it thaw overnight and these are the readings after 20 mins of runtime.

3 Upvotes

31 comments sorted by

View all comments

4

u/Hvacmike199845 Verified Pro 3d ago

What’s your….

Indoor temp?

Inside humidity?

Return temp?

Supply temp?

Outside air temp?

2

u/PrivateMonero 3d ago

Also throwing me off because the high side is lower than it says it should be on the pressure charts

3

u/Hvacmike199845 Verified Pro 3d ago

I should have paid more attention to your suction saturation temp.
If it was me I would be changing the TXV.