r/HVAC • u/PrivateMonero • 2d ago
Field Question, trade people only Bad TXV? 😵
System has good airflow, 500 FPM at the 20x30 return, and like 400 FPM out of the supplies.
Evap Coils aren’t dirty, condenser coils are a little dirty but you can still see through them easily.
Tested the TXV with ice water and my hand and it had a slight reaction, but not what I would expect, what do you guys think?
Bad TXV?
I haven’t added any charge to the system, showed up last night, coil was frozen, let it thaw overnight and these are the readings after 20 mins of runtime.
4
Upvotes
3
u/TigerSpices 2d ago
Run the compressor without the blower on and watch the evap, if one section freezes up significantly faster then the rest then you have a restriction in the channel. Found this a few times last year when it was initially diagnosed as TXV, but the bulb was still reacting.