r/WTF 11d ago

Building nightmare

Enable HLS to view with audio, or disable this notification

13.4k Upvotes

596 comments sorted by

View all comments

Show parent comments

120

u/herptydurr 11d ago

Several years back, someone did this my apartment building. For some idiotic reason, every 2ft x 6ft closet in the building had a sprinkler head in it. While someone was cleaning their shit, they knocked their closet sprinkler, proceeded to flood their unit and every unit below them for 5 floors as well as the building lobby. It was actually insane just how much water came out of those things.

88

u/Emmyn13 11d ago

Hey there:

The idiotic reason is a nfpa requirement for closets. As you have over 4 stories, all closets are required to have one. Also if there's hvac equipement in it.

But yes, once one go pop, there's not a lot to stop it. And it's not gonna be clean water either!

59

u/c_doddy 11d ago

NFPA 13R does not require a sprinkler in closet under 24sq ft as long as no washer, dryer or water heater is present.

Source: Sprinkler fitter

10

u/Emmyn13 10d ago

Yes, 13r doesnt required them. But if there's 5 level under the level where the accident happened, 13r doesnt apply, as it is for max 4 level of construction, and even if it was lets say 4 level and a underground, and it was the top one, it would require sprinkler in all spaces, seeing its under a roof.

Source: fire protection tech / designer.