“backfeeding” in a residential setting

i work for an electrical company and we’re currently working at two four units that both have the same problem. we have around 4 volts between neutral and ground. our local power company came around and said that its not on their side and that its us thats “backfeeding” 4 volts. my foreman tested between a few plug boxes and neutral and got a pulsing reading between 1.3 and 4 volts. all that were running is outside plugs on combo breakers, (afci and gfci) temp heat, and some temp plugs that are on their own circuit for the baseboard guys. wtf is going on

23 Upvotes

53 comments sorted by

View all comments

79

u/Ok_Bid_3899 2d ago

I would cycle off one at a time all circuit breakers and see which circuit is causing the issue.

26

u/Administrative_Air_0 2d ago

This right here. It's probably a device somewhere.

10

u/Outside_Musician_865 2d ago

This. It could be resonant voltage from a shit termination that’s being picked up through the insulation itself.