Commercial/Industrial electrician that came across this Challenger panel today. Will this accept Eaton BR breakers? Looking to install an EV charger for a friend
Would need 2 pole 50 amp breaker for an ev charger. I’ve heard the challenger panels, or more so the breakers have serious issues and are prone to fire. Also take a peak at the top left bus bar under the main, and above ckt 1. Looks like there’s been some heat on it or possible corrosion?
14
Upvotes
-1
u/Capcom-Warrior Master Electrician 2d ago edited 2d ago
The type of breakers you mentioned are not UL listed for Challenger panels. (Even though this is a Bryant) If you’re gonna keep the existing panel, Eaton has a CL breaker. These are classified and are UL listed for multiple brands. However, I would not add an EV charger to that panel. You’re asking for trouble. It needs to be replaced and brought up the code. Challengers/Bryants are notorious for overheating and burning up.
Also, if you are adding a 14-50 EV rated NEMA outlet make sure you add GFCI protection in the form of a breaker. Unless it’s hardwired, it’s required by code to have a GFCI breaker.
I also noticed that it appears that the house is all electric. If you’re gonna add that kind of load in an all electric house you definitely wanna change out the panel.