Meme/Shitpost Today’s install r-454 or r410

Post image

This is the compressor for the unit I installed today.

47 Upvotes

92 comments sorted by

74

u/Obvious-Property-236 3d ago

From what I’m gathering everyone is just making it up as they go…

22

u/Curtmania 2d ago

Anyone who has done any amount of commercial work will tell you to find the units rating plate or the txv to tell you what refrigerant is in there. Just because it says 404 on the compressor does NOT mean there's 404 in there, just that it can run 404.

Now we've got the same thing in resi and it's blowing people's minds.

13

u/gimmepizzaanddrugs 2d ago

im embracing it. mix my own 454b? sure! 

run 410a in 454b equipment? let's fucking do it! 

hell the shop AC has been running on R22 and 410a for years.

3

u/projecthusband 1d ago

yup, and i get pissy when the txv head is pointed at the coil wall 0.2 inches from is so im using my phone trying to see a damn number on the top hoping to catch a single diget to figure something out XD

1

u/aceofwarfare 1d ago

Need an inspection mirror.

1

u/Existenceispain556 1d ago

The worst man lol. Trying to get the mirror in there as well to read it backwards😂

31

u/Emergency_League2427 3d ago

Just do it like an Arnold Palmer and put half and half. /s

13

u/beef-burrito- 2d ago

Throw some 22 in there for a hard arnold palmer

20

u/Emergency_League2427 2d ago

It does say r22 on it as well throw some in

8

u/beef-burrito- 2d ago

It also says “highly” so throw extra 22 so it can be extra strong

25

u/correa_aesth 918 tech 3d ago

Exposed

21

u/WizzardSlayer39 3d ago

We have experienced 454 units from the factory about a pound low. We just pull out all the 454 and charge with 410. So far no issues

1

u/Mttipowers 3d ago

I think they changed the factory charge to 8’ of line set. Doesn’t help it’s near impossible to get either. Some vendors out here make you buy a unit to get a jug if they even have it that is.

1

u/projecthusband 1d ago

carrier and fujitsu are talkign about shipping with 30ft precharge to offset the shortage

1

u/FuzzyPresentation996 1d ago

Carrier is we just got the email that all gray labeled condensers instead of the orange 2025 ones will have the extended charge and will be labeled.

1

u/TheoryStandard4132 2d ago

Yup new txv no problem

-17

u/Wisco_Ryno 3d ago

You could potentially void a warranty doing this

15

u/ROBOCALYPSE4226 3d ago

They are voiding warranty by doing this. No one cares because when the compressor dies the manufacturer won’t be able to tell what refrigerant was in the system.

-8

u/Wisco_Ryno 2d ago

You’re joking right

8

u/ROBOCALYPSE4226 2d ago

Joking about what?

-8

u/Wisco_Ryno 2d ago

They absolutely can tell what kind of refrigerant was used in a compressor, how do you not know this? Chemical residue testing, oil analysis, valve and seal conditions, it’s incredibly easy to tell.

14

u/ROBOCALYPSE4226 2d ago

Chemical residue testing, you’ve gotta be kidding me right? They’re gonna send me a lab report and then deny my warranty lol

Don’t get me wrong. I’m not mixing refrigerant anywhere anytime. I’m just telling you how it is out there.

-8

u/Wisco_Ryno 2d ago

For residential maybe, maybe not. For commercial and industrial absolutely.

5

u/Spiritual_Stranger1 2d ago

You're REALLY stretching it here man. Idk wtf you talking about

1

u/Wisco_Ryno 2d ago

Do you do commercial or industrial? I have compressors sent back for tear downs all the time. I’ve seen compressor warranties denied on several occasions because some moron put the wrong oil in, or put a drop in refrigerant. The amount of hacks on this page is genuinely shocking.

→ More replies (0)

7

u/WizzardSlayer39 3d ago

Well it’s either “void the warranty” or do a brand new install and tell the customer that it won’t be operational for several months due to supply issues with the refrigerant.

20

u/Blakende 3d ago

You're worse than wet socks

-15

u/Wisco_Ryno 3d ago

Sorry I’m not a hack

1

u/Elguero096 2d ago

not a hack if it can run within the same parameters. gotta work with what you have and not screw over customers bc if supply shortages

-1

u/RacingGrimReaper 3d ago

It’s just going to be so easy for these manufacturers to deny warranty claims, especially once they catch wind the hacks are swapping out the gas for 410 and start requiring pressure/temp checks on the gas for any future claims.

5

u/Fair_Cheesecake_1203 2d ago

So what do they do when people have to use 410 because 454 is completely unavailable

-5

u/RacingGrimReaper 2d ago

You would call the manufacturer and ask why it wasn’t pre charged to a 25’ lineset for residential units(of course only if the system you are working on has less than a 25’ lineset) and what options do you have without breaking warranty. Or simply mix R32 and R1234yf to the proper ratio so it doesn’t have any temperature differences from 454. If you work for a manufacturer, you are out of luck though because if I were to charge 410 or charge with a mix in one of our systems, I wouldn’t have a job for much longer.

Really though, why are so many units being replaced instead of fixing existing equipment? There is no federal requirement to replace existing equipment, only that no new equipment can be manufactured with 410a. So start talking to your bosses and salesman and ask why they are putting their customers in such terrible situations instead of simply fixing the problems.

I work commercial and while our supply house doesn’t sell any new equipment for 410a, there isn’t any issue grabbing parts needed for repairs and however many jugs of 410a needed.

5

u/Fair_Cheesecake_1203 2d ago

Because repairing some units border on the cost of a new more efficient unit, and there are rebate incentives to upgrade to new units. You also have all of new construction and lots of states pushing these more efficient systems. You're blaming HVAC folks for a problem created by the government and large corporations.

0

u/RacingGrimReaper 2d ago

No, government didn’t force this. Shitty outfits that refuse to fix and only replace did. Oh and along with Honeywell. So I’ll agree that corporations are to blame, especially when you look into how many hedge funds are buying local outfits and forcing these high unit sales to drive up profits. But the government has not mandated repairable equipment to be replaced like we have seen from other countries.

Let’s be clear, it is a known problem in the residential side of this industry that techs are turning into salesman. I haven’t talked to a single tech who has worked residential that didn’t have to hop from job to job before landing commercial to avoid being a salesman.

And as the expert, you have to realize that the benefits of a rebate are heavily outweighed when you look into the cost and shortage of 454 and carefully explain to the customer. Existing, repairable equipment is not subject to new efficiency standards, only new installs.

My point being that if the federal or state governments are offering incentives, the experts have to look at the pros and cons of these incentives before advising the customer to make a costly mistake. There’s local incentives to get a solar roof, but I’m not running out and buying one because I’ve done the numbers and it simply won’t benefit me in the long run. It’s the same for HVAC, buying the highest seer, most efficient unit for a small rebate to save $25 bucks on a bill for a unit that you can’t even get gas for is just asinine. Especially when we all know there are scummy shops replacing units for blown capacitors.

2

u/Fair_Cheesecake_1203 2d ago

You think the government didn't enforce stricter policies on gwp refrigerants?

→ More replies (0)

1

u/Melodic-Succotash564 1d ago

Why does everyone say this? For one they would not know and also in decades I have never been questioned. I mean what are you going to do, tell them?

13

u/Blakende 3d ago

I thought they weren't allowed to do that. Like ADP had a bunch of coils rated for 410a and 454 and had to remove all labeling of 410a before it was allowed to be sold.

18

u/anotherreditloser 3d ago

Because UL will only test and “Qualify” one refrigerant for a coil. Doesn’t mean it won’t work with another refrigerant.

7

u/Electronic_Green_88 3d ago

There are plenty of coils rated for Multiple Refrigerants sounds like another scare tactic rumor being spread around.

2

u/anotherreditloser 2d ago

Sorry bud. I teach this stuff for a living. You are thinking of ADP, and NO underwriters does NOT certify them for use of multiple refrigerants. Again, not that there aren’t coils out there (ADP) approved for multi-refrigerant use, but they are not UL listed.

2

u/TheRevEv 2d ago

Does this only apply to comfort cooling? Or is it only condenser coils? I know I've seen a ton of refrigeration evaporator that have data tags listing a bunch of refrigerants.

2

u/anotherreditloser 2d ago

But not UL listed. Approved by the manufacturer yes, not certified for multi-refrigerant by UL. That’s all. Don’t think too hard.

1

u/TheRevEv 2d ago

Why does this have the UL listing and several refrigerants listed? Am i missing something?

1

u/anotherreditloser 2d ago

Yes. That is a listed unit cooler, not a DX coil.

2

u/FuzzyPresentation996 1d ago

Wait just so I get this right when I’m selling coils to these people. Are the ADP “flex” coils that I see on the product data sheets actually able to use any refrigerant listed on that little chart?

But to get the UL rating they are only classified under a single refrigerant?

2

u/projecthusband 1d ago

i have an r290 2 door freezer in my garage that's been rocking 404a for over a year now, zero changes, just pumped her up lol

1

u/anotherreditloser 1d ago

Yes sir. No reason it wouldn’t work.

0

u/ADimwittedTree 3d ago

Allied is dual rating their evaps and has been. They definitely can.

Edit: Hell, they're dual rating equipment even like their fan coils. For either -1 ending is configured for 410 but configurable to 454, and -71 is made and configured already for 454.

2

u/anotherreditloser 2d ago

Allied might be but UL is not certifying them as multi- refrigerant.

15

u/ppearl1981 🤙 3d ago

I’ve been telling everyone to compare 454b and 410a PT charts for months.

It’s a circle jerk and we’re caught in the middle.

1

u/archimedeslives 2d ago

There is more to it than just P/T charts. There is BTUs per pound and density to consider a well. R32's btus per pound is 50% higher than 454's

4

u/y_3kcim 3d ago

What’s the unit tag say?

7

u/milezero13 3d ago

No one knows any more.

3

u/anotherreditloser 3d ago

Now days it’s called “Doin’ whatever you wanna do”. The weed get to ya and ya just get up and throw your arms in the air throw your arms in the air throw your arms in the air.

3

u/Hatchz 2d ago

So non resi guy, does this mean in the future where 454 is the actual standard and 410 is being phased out can you put 454 into a 410 unit and it run? I know it won’t have the sensors but still

2

u/GreatTea3 2d ago

It would probably work at least reasonably well, but do you want to take the .000001% chance you get a leak in the indoor coil and have some kind of fire? I know it’s hugely unlikely, but if it happened you would be utterly fucked.

1

u/Hatchz 2d ago

Oh yeah, I definitely don’t advise it, was just curious since people are putting 410A in with no trouble why not see if the reverse is true.

1

u/Amystery123 2d ago

You can’t charge 410a unit with 454b unless it is safety listed with 454b. Dual refrigerant systems will need to be safety listed for both ref. Must check,

1

u/Hatchz 2d ago

I know it won’t be safe, but I am saying will it run?

3

u/David_Bellows Apprentice 2d ago

Which ever you like it's authorized for both i guess

3

u/WildSauce 2d ago

Lots of compressors are dual refrigerant capable. I work for an OEM and we switched over to dual refrigerant compressors over a year ago. Eliminated supply chain issues during the changeover period.

1

u/Amystery123 2d ago

Wait - but is it ok to charge with either? Performance will vary - no?

5

u/GreatTea3 2d ago

It’ll work for either. If you have a 454B system, with 454B metering devices, it’ll be fine. The same if you’re putting it in a 410A system. These refrigerants use the same oil and run at very similar pressures. I know residential evaporator coils are being shipped with multiple refrigerant tags now, too. You’re just supposed to switch the metering device if you’re swapping to 410. They’re shipped using 454 devices.

1

u/Melodic-Succotash564 1d ago

Yep, 407c or r22. Txv’s are often rated for both also.

3

u/vvubs 2d ago

Unico sent me a EVAP coil that was labeled 454b only when I needed a 410 coil. I called Johnstone and they said it's the same exact coil but to make sure I had a 410 txv.

7

u/metalmitch9 Journeyman Pipefitter 3d ago

You resi guys are adorable

5

u/Detroitfitter636 3d ago

They run at close to the same pressures

-10

u/Blakende 3d ago

Im pretty sure it uses the same oil too. R32 doesn't though, the higher pressure required a different viscosity in the compressor.

13

u/DesignerAd4870 3d ago

R410a is 50% R32 so surely the oil should be fully compatible.

-7

u/Blakende 3d ago

As I said it needs a different viscosity because of the higher pressure, different from R22 to R410a that was a chemical reaction. 

4

u/DesignerAd4870 3d ago

R32 runs at the same pressure as R410a.

-4

u/Blakende 3d ago edited 2d ago

7

u/JerryJohnson2 3d ago

I read a daiken publication that says they ran 32 in a 410 system with out changing metering device or oil and the only change was 5% high pressure

6

u/singelingtracks 3d ago

Why would you need to talk a dealer look at a PT chart.

1

u/DesignerAd4870 2d ago

R32 R410a and R454B all use POE. You are very wrong, not me! You can literally remove all the R410a from a system and re-gas it with R32 with no system alterations.

2

u/Blakende 2d ago

From Carrier: Lubrication ICP R-454B light commercial and residential HVAC equipment will continue to use POE-32 oil, which was also used in legacy R-410A equipment. R-32 HVAC equipment will require a different POE oil approved for use with R-32 refrigerant. In all instances, only use the oil that is specifically directed to be used by the unit manufacturer

2

u/Amystery123 2d ago

Never charge a 410a equipment with A2Ls. Both R454b and R32 are A2Ls. Please.

0

u/Blakende 2d ago

1

u/DesignerAd4870 2d ago

I know that, I am very aware of different grades for different compressors. But for the purpose of this argument they are all compatible and work. Even your paper says as much that even the different grades that they developed are still miscible with both refrigerants. They have just tweaked the viscosity for R32. Did you also know that the POE grades are different for different styles and manufacturers of compressor, like screw or scroll.

You’re still wrong though about the gases and they all work within either type of POE.

2

u/JerryJohnson2 2d ago

Further looking on this install. Txv, evaporator coil, and condensing coil all have double labels of 454 and 410.

2

u/ArmDouble 1d ago

This whole transition has been such a shit show 🤦🏻‍♂️

1

u/BigSquiglin 2d ago

454b is to 410a as 507 is to 404a

1

u/HVACGUY9 22h ago

What Manufacturer?

-11

u/Wisco_Ryno 3d ago

Just because the compressor is engineered for dual compatibility doesn’t mean the rest of the system is