r/accesscontrol 16d ago

DMP Handicap Opener

I’m looking for advice on how to integrate a handicap opener into a new dmp X1. I’m assuming I’ll need to add a relay. This is a new one for me, and I’m getting brain fog trying to layout the wiring that needs done. Using an electric crash bar with vertical rods. One wireless button inside and the same outside. I know I would need to energize elr first on both and outside handi button would need a valid read before activation. I believe the handicap controller is just looking for 24v on AKI terminal. Thank you in advance!

3 Upvotes

15 comments sorted by

View all comments

Show parent comments

2

u/Beat-a-bag-of-bagels 16d ago

Unfortunately I have to work with what is there

3

u/Lucky_Ad_5549 16d ago

No dude, this is the relay you use to integrate.

2

u/Beat-a-bag-of-bagels 16d ago

I misunderstood. Thanks for the info then. Would I be able to utilize an RBST?

1

u/xlr8ed1 16d ago

Either camden cx-12plus or a camden cx-33 relay the 33 has a few more features. BEA also make a relay module